Fire and smoke dampers often appear in the model late, after the ducts are already sized. Then the fan pressure looks short once those fittings are actually in the path.
I try to place the damper as a MagiCAD fitting, or as a product with a known pressure drop, in the correct fire-compartment wall, not as a 2D symbol on the drawing only. If the calculation does not see the damper, the index run is too optimistic. If the product data gives a loss at a stated flow, I use that and check it again after sizing, because the figure changes if the duct size or the airflow changes. A placeholder with a rough fixed drop is fine for an early pass, but I would not issue the fan duty from that number alone.
Coordination matters as much as the pressure figure. The damper needs space for the blade, for access, and for the wall sleeve. A duct that was clear of a beam may no longer be clear once the damper and the insulation are in. After moving a riser or adding an offset I rerun both the airflow and pressure calculation and the clash check, otherwise the report and the model drift apart — the same problem as with moved terminals, see keeping terminal flows and duct sizing aligned.
How do you handle this on your projects: do you put dampers in before the first sizing, or add them after coordination and then resize? And do you take the pressure drop from the manufacturer product or from a typical fixed value?
I try to place the damper as a MagiCAD fitting, or as a product with a known pressure drop, in the correct fire-compartment wall, not as a 2D symbol on the drawing only. If the calculation does not see the damper, the index run is too optimistic. If the product data gives a loss at a stated flow, I use that and check it again after sizing, because the figure changes if the duct size or the airflow changes. A placeholder with a rough fixed drop is fine for an early pass, but I would not issue the fan duty from that number alone.
Coordination matters as much as the pressure figure. The damper needs space for the blade, for access, and for the wall sleeve. A duct that was clear of a beam may no longer be clear once the damper and the insulation are in. After moving a riser or adding an offset I rerun both the airflow and pressure calculation and the clash check, otherwise the report and the model drift apart — the same problem as with moved terminals, see keeping terminal flows and duct sizing aligned.
How do you handle this on your projects: do you put dampers in before the first sizing, or add them after coordination and then resize? And do you take the pressure drop from the manufacturer product or from a typical fixed value?