On a coordination pass we had to move several supply terminals after ceiling clashes, and the branch flows stopped matching the balancing schedule. I can update the model and run the checks, but I’m not sure what workflow others use to keep terminal data and downstream duct sizing in step as the layout changes.

How do you manage ventilation balancing in MagiCAD/Revit when room terminals and branches keep moving during coordination?

  • Do you rerun system calculations after each coordinated change or at defined milestones?
  • How do you track room design flow versus terminal flow so the schedule doesn’t quietly drift?
  • Do you size from terminals upstream, or use a different sequence?
  • What do you check in the model before issuing a balancing schedule?

I’m especially interested in practical habits that avoid a last-minute spreadsheet cleanup. If you have a method that has held up on a live project, please share how you set it up.
 
We've run into the same MagiCAD/Revit headache on a couple of healthcare jobs. We stopped chasing every terminal move and settled on a rhythm that actually survived live coordination.

We don't rerun full system calculations after every clash. We batch them at clear milestones: after each major coordination round (usually weekly) and always before any balancing info leaves the office. Small nudges that stay on the same branch get ignored until the next calc pass.

Room design flow stays locked in the MagiCAD space objects from the original load calc. Terminals inherit from the space (or we assign them and then run MagiCAD's air-flow check). A simple Revit schedule comparing space airflow versus the sum of connected terminals flags any drift immediately — no quiet schedule creep.

We always size from the terminals upstream. MagiCAD's duct-sizing tool does exactly that: set the terminal flows, it works the branches back to the AHU. We only re-size once the layout has settled a bit, not on every 50 mm shift.

Before we issue a balancing schedule we always:
- Run MagiCAD connectivity check (no orphaned ducts or unconnected terminals)
- Full system calc (pressure, velocity, damper positions)
- Compare the MagiCAD flow report against the frozen original design airflow list
- Quick visual that every terminal is still in the correct space

The habit that killed the last-minute spreadsheet cleanup was treating MagiCAD as the single source of truth. We stopped exporting to Excel until the very end, and even then only for the contractor's balancing sheet. Everything else stayed live in the model.

It's held up on two projects so far. Hope it saves you some late nights.
 